Alternator Synchronization
Conditions
Conditions
There are five conditions that must be met before the synchronization process takes place. The alternator must have equal line voltage, frequency, phase sequence, phase angle and waveform to that of the system to which it is being synchronized. Waveform and phase sequence are fixed by the construction of the generator and its connections to the system, but voltage, frequency and phase angle must be controlled each time a generator is to be connected to a grid.
Process
In the past, synchronization was performed manually using three-lamp method. Nowadays, the process is automatically operated and controlled with the aid of synchronization relays.
During installation of a generator, careful checks are made to ensure the generator terminals and all control wiring are correct so that the order of phases (phase sequence) matches the system. Connecting a generator with the wrong phase sequence will result in a short circuit as the system voltages are opposite to those of the generator terminal voltages.
The sequence of events is similar for manual or automatic synchronization. The generator is brought up to approximate synchronous speed by supplying more energy to its shaft - for example, opening the valves on a steam turbine, opening the gates on a hydraulic turbine, or increasing the fuel rack setting on a diesel engine. The field of the generator is energized and the voltage at the terminals of the generator is observed and compared with the system. The voltage magnitude must be the same as the system voltage.
Synchronizing lamps
Formerly, three light bulbs were connected between the generator terminals and the system terminals (or more generally, to the terminals of instrument transformers connected to generator and system). As the generator speed changes, the lights will rise and fall in intensity at a rate proportional to the difference between generator frequency and system frequency. When the voltage at the generator is opposite to the system voltage (either ahead or behind in phase), the lamps will be bright. When the voltage at the generator matches the system voltage, the lights will be dark. At that instant, the circuit breaker connecting the generator to the system may be closed and the generator will then stay in synchronism with the system.
Synchroscope
Another manual method of synchronization relies on observing an instrument called a "synchroscope", which displays the relative frequencies of system and generator. The pointer of the synchroscope will indicate "fast" or "slow" speed of the generator with respect to the system. To minimize the transient current when the generator circuit breaker is closed, usual practice is to initiate the close as the needle slowly approaches the in-phase point. An error of a few electrical degrees between system and generator will result in a momentary inrush and abrupt speed change of the generator.
Synchronizing relays
Synchronizing relays allow unattended synchronization of a machine with a system. Today these are digital microprocessor instruments, but in the past electromechanical relay systems were applied. A synchronizing relay is useful to remove human reaction time from the process, or when a human is not available such as at a remote controlled generating plant. Sometimes as a precaution against out-of-step connection of a machine to a system, a "synchro check" relay is installed that prevents closing the generator circuit breaker unless the machine is within a few electrical degrees of being in-phase with the system. (Synchro check relays are also applied in places where several sources of supply may be connected and where it is important that out-of-step sources are not accidentally paralleled).
Synchronous operation
When the generator is synchronized, the frequency of the system will change depending on load and the average characteristics of all the generating units connected to the grid. Large changes in system frequency can cause the generator to fall out of synchronism with the system. Protective devices on the generator will operate to disconnect it automatically.
References
^ Terrell Croft and Wilford Summers (ed), American Electricans' Handbook, Eleventh Edition, McGraw Hill, New York (1987) ISBN 0-07013932-6 pages 7-45 through 7-49
^ Donald G. Fink and H. Wayne Beaty, Standard Handbook for Electrical Engineers, Eleventh Edition,McGraw-Hill, New York, 1978, ISBN 0-07020974-X pp. 3-64,3-65
External links
Flash Animation on Alternator Synchronization.
Categories: Electric power
by: gaga
Mike's Truth About Abs Program-Truth About Abs Read this Before Opening High-Yield Savings Accounts Sense Not Size Eat This- Don't Eat That! Darragh Macanthony Will Not Stand In The Way Of Any Peterborough United Players Who Want To Move On Visit Halifax Nova Scotia How To Deal With Roof Damage Stunt Race Fx Coping withe the Demands of Seasonal Giving - The Little Prince Series The Straightforward Power of Art Where Does Dry Eyes Originate? Why Get Well Hampers Are So Great Outrageous Dui Arrests: Five Of The Best