Schools in Beijing to warm water heating systems engineering case description - heat pumps, solar, geothermal heating, heating - heat pump industry
Schools in Beijing to warm water heating systems engineering case description - heat pumps
, solar, geothermal heating, heating - heat pump industry
It is understood that a school in Beijing Ground Source Heat Pump Air conditioning Project Winter running field test showed " Solar Energy + Ground source Heat Pump + Water to warm, "is an ideal heating system worth using.
Project Overview The project covers an area of 71,322 square meters of total planning, including planning of construction land area of 57,332 square meters, total building area of 35,800 square meters, from the primary and secondary school buildings, laboratory building, a small hall, apartment buildings, canteens , stadiums and buildings or building component.
Use ground-source heat of the project Pump System as the end of all buildings with hot and cold sources of energy delivery systems, in addition to sports, teachers and canteen apartments, each building heating only heat source in winter, no summer cold source system. Design of ground source heat pump system provides 7 ~ 12 in summer chilled water in winter to provide 45 ~ 40 air conditioning, heating and hot water.
The project ground source heat pump system cooling design load 5892KW, the project ground source heat pump system thermal design load 2499.84KW.
The project teaching buildings, student dormitories, hall and gym with water to warm, teachers quarters, canteen with fan coil units, fan coil and the whole stadium heat exchange with air conditioning units.
The project of underground pipe system endothermic heat load in winter about 1875KW, bustling place in summer load of about 707KW.
Commissioning of the project in winter field measurement and analysis of the situation
1, debugging and running field test
The project on October 25, 2007 start debugging and running, ground recycled water stable temperature 13.6 , 11 1 debugging is completed, and began to heat buildings.
Month after commissioning, the system operation status as follows:
2007 5 to 15 December, two hosts to run four hours later, the average ground heat exchanger inlet temperature of about 3 , the average water temperature is around 7 , there's low unit to protect themselves down, then the end of the average water temperature around 32 , the average water temperature around 28 , the room temperature can meet the design requirements.
2007 16 to 20 December, two hosts to run 3 hours, the underground heat exchanger average water temperature of about 3 , the average water temperature is 6.5 or so, there's low temperature unit to protect themselves down, then end of the average water temperature of 30 , the average water temperature around 26 , then send the wind fan coil temperature of less than design requirements, low temperature water radiant floor heating part of the room temperature can not reach design requirements.
2007 12 31 debugging found that two hosts could not open normally, and finally by increasing the ground water flow heat exchanger, two heat pumps host can run about 3 hours, underground heat exchanger The average water temperature of about 3 , the average water temperature of about 6 , for 5 days, units of low-temperature shutdown protection of their own, then the end of the average water temperature around 27 , the average water temperature around 23 , the room temperature can not be meet the design requirements.
2008 1 5, a heat pump through the opening, while conditioning off and the floors do not use the room, the supply of sub-periods and functional apartments canteen (noon and evening) and classroom building, buried underground at this time for The average water temperature of heat is about 3.5 , the average water temperature is about 6.7 , the end of the average water temperature around 32 , the average water temperature is 28 , room temperature, the improvement is a good choice for heating.
Baoliao Hotline :020-22374965 Contributors E-mail : hellomily@qq.com Edited by: sub-YinSpeed chain activities: Respect and promotionHeavenly Prize and other vehicles you get to vote2010 5 28 Day? May 29 2010, heat pumps, solar FairHC Network "Hailin Cup" 2010 China Top Ten Brands Award heating system http://www.articlesbase.com/rugby-articles/schools-in-beijing-to-warm-water-heating-systems-engineering-case-description-heat-pumps-solar-geothermal-heating-heating-heat-pump-industry-2641771.html
Robert Hirsch Lightyear Wireless: Showing Entrepreneurs how to "Manage" a New Career Path Lennox Solar Powered Heat Pumps and Air Conditioners now available I Want Solar Power For Home - Now What? Gianni Truvianni's "South Africa 2010", Reid's Last Minute Goal Gives New Zealand A Well Earned Draw Against Slovakia Five Questions Regarding Solar Residential Panels Why Has This New Guy Dumped Me Help Me PLZ On Death And Dying - A New Way To See Things! Proven Weight Loss Diets That Create A New You The Power Of Solar Panels The Green Electrician For Quality Solar Panels The Benefits Of Solar Panels The Amazing Savings Solar Panels Can Do For You Changing Your Carbon Footprint With Solar Panels